So I just got done reading Steve Terry's article:
Electrical Diversity
But theres something that I want to make sure I completely understand here.
Steve gives an example: “Why, 32 twenty amp loads, of course. I’ve got a 20 amp dimmer feeding each circuit, the connector strip and the gridiron junction box are fully rated, and I have 3600 amps of power feeding the dimmer system. In fact, the light plot for my next production calls for 32 - 2000 watt fixtures on the first electric, so I’ll have an extra 400 watts per circuit.”
And then Steve begins to explain why its wrong. But I want to make sure I understand why this is wrong.
In one way the electrician is right because each circuit will be 20 amps and 2400w. But the thing that makes him wrong is the fact that the 2 SO cables running from the grid to the raceway will have 32 conductors and 4 ground and the 32 conductors means that they can only have 60% of ampacity according to table 520.44 correct? So therefore each circuit can only be loaded up to 12 amps or 1440w. Is that right? And so if for whatever reason I absolutely needed every dimmer on that electrical to be loaded to 2000w each (is my terminology correct by the way?), I would need to run individual cable from the grid to each circuit? Because even if I had a 4 conductor multi-cable, then each dimmer could only be loaded to 1920w each right?
And Also, as far as the temperature rating in the same table, the amperage listed under each table is the amount of amps that size wire can be loaded to before overheating correct? However I know not to exceed the amperage listed on the far right of the table under "Maximum rating of overcurrent device". This is just more of a theoretical question.
Sorry for so many questions, I just wanted to make sure I understood this right.
Electrical Diversity
But theres something that I want to make sure I completely understand here.
Steve gives an example: “Why, 32 twenty amp loads, of course. I’ve got a 20 amp dimmer feeding each circuit, the connector strip and the gridiron junction box are fully rated, and I have 3600 amps of power feeding the dimmer system. In fact, the light plot for my next production calls for 32 - 2000 watt fixtures on the first electric, so I’ll have an extra 400 watts per circuit.”
And then Steve begins to explain why its wrong. But I want to make sure I understand why this is wrong.
In one way the electrician is right because each circuit will be 20 amps and 2400w. But the thing that makes him wrong is the fact that the 2 SO cables running from the grid to the raceway will have 32 conductors and 4 ground and the 32 conductors means that they can only have 60% of ampacity according to table 520.44 correct? So therefore each circuit can only be loaded up to 12 amps or 1440w. Is that right? And so if for whatever reason I absolutely needed every dimmer on that electrical to be loaded to 2000w each (is my terminology correct by the way?), I would need to run individual cable from the grid to each circuit? Because even if I had a 4 conductor multi-cable, then each dimmer could only be loaded to 1920w each right?
And Also, as far as the temperature rating in the same table, the amperage listed under each table is the amount of amps that size wire can be loaded to before overheating correct? However I know not to exceed the amperage listed on the far right of the table under "Maximum rating of overcurrent device". This is just more of a theoretical question.
Sorry for so many questions, I just wanted to make sure I understood this right.