Vertical L-shaped steel channels located on the upstage sides of the proscenium opening and extending up to the gridiron. The smoke pocket serves two purposes: 1) to provide a guides for the edges of the fire curtain, and 2) to provide a seal (though rarely air-tight) to prevent smoke from a fire from moving from the stage area into the auditorium.
The upstage side of the smoke pocket is often used instead of the plaster line as a basis for which all measurements are taken, as temporary show decks and scenery cannot interfere with the operation of a theater's fire curtain.
The upstage side of the smoke pocket is often used instead of the plaster line as a basis for which all measurements are taken, as temporary show decks and scenery cannot interfere with the operation of a theater's fire curtain.
...
NFPA 80
20.6.5 Vertical Guide Pocket
20.6.5.1 Vertical guide pockets shall be used on all fire safety curtain assembly installations.
20.6.5.2 Vertical guide pockets shall contain the vertical edges of the fire safety curtain assembly and the guide mechanisms used both to guide the fire safety curtain assembly and the prevent binding during operation.
20.6.5.3 Vertical guide pockets shall extend vertically from the stage floor to a point above the top of the open fire safety curtain assembly and shall be fastened or welded to the proscenium wall.
20.6.5.4 Vertical guide pockets shall be fabricated using a minimum of structural steel channel and 1/4" (6.4mm) steel plates or 1/4" (6.4mm) thick steel framed shapes and plates.