So this will be investigated and fixed in the near future-- but for right now this has me stumped.
We're troubleshooting a flickering circuit, we cross patch and determine it's somewhere between (inclusive of) the pigtail to the dimmer rack. While repatching to the original circuit (fumbling in the dark) we accidentally touch the hot pin of the cabling leading to the fixtures to the hot pin of the female stage pin of the bad circuit (N and G pins are not touching) and the fixtures light up.
In order of testing:
Fixture 1 plugged into Pigtail 1= works normally (other than intermittant flicker)
Fixture 1 plugged into Pigtail 2= works normally, no flicker
Fixture 2 plugged into Pigtail 1= works normally other than flicker
Fixture 1 H pin touching Pigtail 1 H pin= fixture lights up
Fixture 1 H touching Pigtail 2 H= nothing happens
Fixture 2 H touching Pigtail 1 H= nothing happens
Fixture 1 plugged into Pigtail 1 normally= fixture lights up
Fixture 1 H pin touching Pigtail 1 H= fixture lights up
Fixture 1 N pin touching Pigtail 1 N= breaker pops (pretty instantly)
I realize I listed some things multiple times, but did so to show that nothing changed during testing and definitively where the breaker tripped. There are other grounded fixtures on the pipe with these.
Up for ideas here-- I'm thinking there must be 2 faults in 2 different places. One would likely be a N-G short on the Fixture 1. However that does not explain why the breaker tripped on N-N and if this were the only problem then the fixture would light up when H was touched to pigtail 2.
We are taking precautions and most of the circuits involved are locked out at the moment. Kids this is a professional theatre with professional technicians with the experience to work on this safely-- don't mess with electricity if you aren't competent to do so.
We're troubleshooting a flickering circuit, we cross patch and determine it's somewhere between (inclusive of) the pigtail to the dimmer rack. While repatching to the original circuit (fumbling in the dark) we accidentally touch the hot pin of the cabling leading to the fixtures to the hot pin of the female stage pin of the bad circuit (N and G pins are not touching) and the fixtures light up.
In order of testing:
Fixture 1 plugged into Pigtail 1= works normally (other than intermittant flicker)
Fixture 1 plugged into Pigtail 2= works normally, no flicker
Fixture 2 plugged into Pigtail 1= works normally other than flicker
Fixture 1 H pin touching Pigtail 1 H pin= fixture lights up
Fixture 1 H touching Pigtail 2 H= nothing happens
Fixture 2 H touching Pigtail 1 H= nothing happens
Fixture 1 plugged into Pigtail 1 normally= fixture lights up
Fixture 1 H pin touching Pigtail 1 H= fixture lights up
Fixture 1 N pin touching Pigtail 1 N= breaker pops (pretty instantly)
I realize I listed some things multiple times, but did so to show that nothing changed during testing and definitively where the breaker tripped. There are other grounded fixtures on the pipe with these.
Up for ideas here-- I'm thinking there must be 2 faults in 2 different places. One would likely be a N-G short on the Fixture 1. However that does not explain why the breaker tripped on N-N and if this were the only problem then the fixture would light up when H was touched to pigtail 2.
We are taking precautions and most of the circuits involved are locked out at the moment. Kids this is a professional theatre with professional technicians with the experience to work on this safely-- don't mess with electricity if you aren't competent to do so.