Okay okay so I know I've asked a lot of electricity questions lately. And I swear I'll stop pretty soon.
Just got three more for you right now
Okay. So First, can
Arc flash happen just from you hooking up a
dimmer rack to a
disconnect? Or do you have to be doing repairs on it or something else for
Arc flash to occur?
Second, Lets pretend youre on tour and you're using three
phase on your tour. But then, you get to a building that has single
phase only! How do you hook up to the
disconnect? I mean if your rack can handle single
phase. And if your rack cant handle single
phase, do you just tell them you cant do the show or what?
Third, Let's pretend youre on tour and you're using single
phase on tour. But then you find out your
venue has three
phase. So I know it's possible. But do you hook up two phases and nuetral and
ground and leave the third
phase un-used, or one
phase, nuetral,
ground and two phases un-used? And if you have one of the phases that you're not using, and it's not connected, is it bad if your
disconnect is on but you have nothing plugged into one of the legs?
So a little more than three questions, sorry.
As to your second question: this is a fairly common scenario, and one that is anticipated by
NEC section 520.53 (O)(1), which states:
Neutral Terminal. In
portable switchboard equipment designed for use with 3-phase, 4-wire with
ground supply, the supply
neutral terminal, its associated busbar, or equivalent wiring, or both, shall have an
ampacity equal to at least twice the
ampacity of the largest ungrounded supply
terminal.
Exception: Where portable switchboard equipment is specifically constructed and identified to be internally converted in the field, in an approved manner, from use with a balanced 3-phase, 4-wire with ground supply to a balanced single-phase, 3-wire with ground supply, the supply neutral terminal and its associated busbar, equivalent wiring, or both, shall have an ampacity equal to at least that of the largest ungrounded single-phase supply terminal.
What this means is that if a
portable dimmer rack or pack does not have an internal method of switching between three-phase and single-phase (as most large racks do not), it must have a 200% rated
neutral terminal.
Why? Because it is assumed that the
road electrician, when confronted with a single-phase service for his three
phase rack is not going to say "Gee, Mr. Merrick, we can't do a show tonight--we only have single-phase". He or she is going to take the two most lightly loaded phases of the
dimmer rack and connect them to L1 of the single-phase service, while the third
leg will get connected to L2 of the service. This is a classic "show must go on" event. This is fine, as long as the rack
neutral terminal can handle the overcurrent caused by the imbalance. Any Listed rack will be able to do so.
For your third question, it is possible to connect a single-phase, 3-wire plus
ground rack to a three
phase service. You would simply not connect anything to the third
phase of the service, as you would only have an L1 and L2
conductor on the
dimmer rack. You would connect the
neutral normally, as well as the
ground.
As to your first question, there is a difference between
arcing and
arc-flash. Arcing can occur when a
connector is made or broken under load. An
arc-flash is the result of an arc being drawn between
phase and
ground, between two or more phases, or
phase and
neutral, where the full
fault current of the source flows into the arc--which can be tens of thousands of amps or more. Both arcs and arc-flashes are bad, but the latter is catastrophic. An
arc-flash has a number of causes that are outside the scope of this discussion.
As an iron-clad safety rule, portable dimming equipment should never be connected or disconnected with the source energized.
Finally, please see the Glossary entry
Qualified Person, per the NEC. Realize that the
NEC section 520-53 (P)states:
Qualified Personnel. The routing of
portable supply conductors, the making and breaking of supply connectors and other supply connections, and the energization and de-energization of supply services shall be performed by qualified personnel, and
portable switchboards shall be so marked, indicating this requirement in a permanent and conspicuous manner.
Exception: A portable switchboard shall be permitted to be connected to a permanently installed supply receptacle by other than qualified personnel, provided that the supply receptacle is protected for its rated ampacity by an overcurrent device of not greater than 150 amperes, and where the receptacle, interconnection, and switchboard comply with all of the following:
(a) Employ listed multipole connectors suitable for the purpose for every supply interconnection
(b) Prevent access to all supply connections by the general public
(c) Employ listed extra-hard usage multiconductor cords or cables with an ampacity suitable for the type of load and not less than the ampere rating of the connectors.
ST