At some
point I hope the pictures are posted. I’ll
send them to Mayhem tonight to see if he beats Dave to the task on posting them. I was once sent a step by step set of directions for posting pictures here and it went right over my head. If I can find them, I’ll attempt again.
So far you both are doing just fine in thinking
thru a problem and have at all times been right on the cusp of an answer. Perhaps not the proper technical answer or the specific cause of it much less the three possibilities for the cause, (might be four at this
point) more in a related to and similar things centered around the same things one might notice, but still right on the cusp of an answer.
There was no damage or melting to the
plug body itself except that the retaining part at the rear of the pin was broken - not by way of heat (probably); more from concussion such as from an un-lucky dropping of the
adaptor on the pin in just such a way. Than again the pea and the princess type theory of something inside the other
connector or something wrong with it is also a possibility in causing it to break and slide backwards. In this pin sliding backwards on a
Bates plug - because there is different types of
plug design thus it’s important, there was lots of room behind the pin for it to do so without shorting to another
conductor. Shorting within this
plug is not the cause given no shorts were noted where the conductors come back together at the
strain relief. In looking at the conductors at the
strain relief, if too tight or conductors were nicked while the
wire was stripped, this could be a cause in other situations but not in this case.
Specifically in a too tight
strain relief, the malleable material such as the
insulation around conductors if forced out of the way - I have seen as little as 1/32" of
insulation between conductors on cables carrying 20 amps and more given the rest of the
insulation is forced out of the way. That
strain relief holds really tight up until the
insulation it’s forcing out of the way, at least the remainder of it allows the
insulation to melt away in a dead short. Than it’s loose again once it’s done melting. (Always read and follow the manufacturer directions on doing a
strain relief. Them little slips of paper are there for a reason, if you have not read it, perhaps you should because there is frequently details that are needed to know. Now if I could only get “professional” tech people to do so. They know what they are doing by way of making their living at doing so - “you trying to tell me my job?”) This especially becomes a problem where the
wire flexes right next to the
strain relief. Conductors move as the
wire flexes and if the
strain relief is too tight, they can cut
thru what little
insulation is left between conductors as the conductors move. Been there, done that on 208v plugs, not pretty.
In nicking the wires you strip, even if not all the way
thru the
insulation, with use and pulling on the wires, those nicks open up in exposing wires. All you need than is either moisture to bridge the gap between conductors or sufficient amperage for a short to occur. As said however, both conditions were not present. Such things were the subject of a PBS special on why some planes started falling out of the sky. In either case, it was noted that neither was the case.
The pins of these plugs a little gap or slit cut in them which serves two purposes over pins of say a Cee Form pin and sleeve
plug that does not have any slits cut parallel to the length of the pin.
The purpose of this slit is two fold. As the pin gets heated up with
current, it allows for expansion and contraction of the pin without adverse effects to it. Second with this slit, it allows some amount of spring to the pin both in retention in the
socket, and even when hot and expanded, allowing the
plug to be removed.
To maintain a proper tension
plug to
connector, it’s necessary for this slot to stay parallel on each of the pins that join with a
socket. With use and abuse this gap in the pin frequently becomes crunched together. Ever hear about not dropping your cables “clunk” on the
stage deck? Beyond possibly breaking the pin loose from it’s housing so it slides backwards within the body of the
plug, or even breaks the outer shell of the
plug, such dropping can cause the pins to
bend or gap to squeeze together. This stepping on them
etc.
These abuse issues and lot number differences between plugs of a specific date in alignment with plugs of another date; much less wee
bit of differences between one brand joining with another while the slotted pin will compensate for some of it, does cause the slot in the pin to be squeezed together at times in use. No big thing take out your handy
pin splitter and correct the problem. Short of re- slitting the pin, it forms a sort of
cone shape in two of the three dimensions. In having a
cone shape
fitting into a parallel slot, naturally it’s going to have less surface contact with the other sleeve it’s connected to. This less surface contact can have a certain amount of heating
effect on the pin when under load but normally not sufficient enough to cause failure. Something to watch with these male pins, but not something that’s normally going to burn down a building. The other reason to watch the gapping of a male
stage pin is because of tension reasons. If the
plug does not have a
bit of resistance as it slides home into a female
connector, it might slide out during a show, much less either it or the female
connector’s gapping is in proper in causing even at times the
current to jump between
socket and pin which causes a lot of heat. These arcs will tend to either weld the connectors together or cause pitting from welding on the surface of the pins and sockets. Pitting is also a bad thing in removing surface area to conduct electricity.
Raised sections from the welding will tend to prevent the other than raised sections of the
plug to contact the female part of it, pitts and recesses while less dire remove that amount of area from contacting the other
conductor. That’s why you don’t
hot patch or in other words
plug in or remove a load from the
power source. In doing so you tend to arc the conductors together in causing this at the first
point of contact. This arc welding can prevent the surface area of a pin from contacting a sleeve with sufficient amounts of contact. (Need to test a
fixture, install a
switch that is designed to turn
power off and on. Need to check a
fixture, turn the
dimmer off.)
Specific to this problem, while the male hot pin was squeezed together, there was no arcing observed on it’s surface, just a change in the color on the pin due to heating.
This heating can be because of a loose screw in holding the
wire even furrled
wire to the pin or sleeve/female
connector. The
wire without good contact to the pin it’s attached to tends to heat up in an extreme when
current flows
thru it at a high resistance due to the means of clamping. Never put a bare
wire under a set screw, never over tighten it. In over tightning it, you cut into the
conductor and by way of pressure on it or specifically those conductors most under tension by the screw, you cause a high resistance load because some of the conductors are really clamped hard together, and some are not as tight. In a loose connection, none of the conductors are really tight to the screw
terminal. As above, some less than others unless in a
ferrule or wrapped in holding the conductors together in a similar way.
Remember that
current follows the path of least resistance. Since a
wire is a path of least resistance it tends to follow it as long as it’s easy to do as if a water hose. Clamp down too tight on the hose and the water will wish to find another place to
escape. Clamp down too loose on the fittings and it’s also going to
escape. This escaping energy becomes heat in the form of resistance to the
current flow. I have another set of pictures TBA demonstrating this in the case of a 100 amp distribution
block when these conditions and others were found on a three
phase 400A
distro panel.
In any case, given
current follows the path of least resistance, it will also tend to flow down the outer round surface of a
conductor because of this. This term is the term “skin
effect.” There is less resistance to
current flow towards the outer parts of the
conductor than in the inner parts of the
conductor that’s all copper and no air as it were. Never cut down the outside of a
conductor cable so it fits within a lug that’s too small otherwise to fit. When absolutely necessary to make the cable smaller, always cut the inner conductors and
bend the outer conductors inwards due to this skin
effect while tying in
power (later).
In the case of a high tension clamping of the
wire to the
plug or any
terminal of it, you squeeze a
conductor in high resistance because of the skin
effect. The
current will still wish to flow to the outer edges around the pressure applied by the set screw. Some parts of the
conductor will be less clamped than other parts of it especially when you don’t use a
ferrule or similar means to ensure all conductors receive the same pressure. The
current will naturally flow to these parts of least resistance. If the conductors are not clamped sufficiently, the individual strands both under screw
terminal and
strand to
strand will than ac to each other in jumping the
current. This arcing than causes heat which melts the conductors jumping in the
current which further causes resistance in even more heat yet.
(Note: this is a very important concept to understand by way of lamps
fitting into sockets or any other electrical joining of materials that other wise are individual conductors.)
Clamp the
conductor too loose, and you have the same problem as above with little arcs of electricity following the path of least resistance much less any movement with the cable will tend to make a higher arcing contact
point with it. Once you get back to the
wire from this clamped junction, you also get back into the classic skin
effect of the
current traveling around a round outer surface of the
wire. In going from clamp to round
conductor, you get into problems mentioned above about cutting those outer strands of a
feeder cable about what happens when the
current has in a cable to get between the area of the clamp, less supported outer areas of a
plug or even inner conductors of a cable that now have an outer layer to go to in a thinned out
conductor. This even to the
point of broken strands of
wire tends to cause heat in the
current following that path of least resistance going from say a
flat section of it with the outer edges less clamped and often broken than to the outer edges of the round
wire. Lots of resistance to a easy flow of
current here.
Also in a turning screw clamping down on individual conductors of a stranded
wire you tend to get the cutting
effect on the
wire that happens as the screw turns it’s way into clamping. Another reason for using a
ferrule or sleeve around the stranded wires. That said, a
ferrule that’s too large to clamp the conductors won’t really support them in keeping them tightly bound under the clamp, nor will the
ferrule in not having bulk around it’s cylinder prevent the screw from just cutting
thru it as if it were screw going into individual conductors.
For this reason, say if I’m wiring a lighting
fixture that uses 16ga
wire, I don’t just use the 12ga
ferrule unless I double up the
fixture’s 16 ga
conductor to 13ga a much closer fit, because the screw in clamping down on it will just cut
thru the
ferrule and even use the
ferrule’s sharp cut
thru edges to further cut into the
wire conductors. Instead I use a 16ga
ferrule sized for the
wire with the 12ga
ferrule sleeved over it so as to provide both a larger area under the set screw for it to hit and also for more metal in using two ferrules for that set screw to tighten into. 16ga inner sleeve than bands the
wire conductors so all receive about the same amount of pressure on them, the outer sleeve closer fits the opening in the hole and provides a second layer of metal between screw clamping down on it and it just cutting because there is no support under it.
Think of the use of a
ferrule as similar to the mechanical advantage you might have in clamping a piece of rope to a woodworking
C-Clamp. First the strands of the rope won't clamp too well to the
C-Clamp in being sufficient to pull it. Next we add a soup can around the
wire. This metal surround around the say 3/4" rope better clamps down on the rope, but does not really encase the rope well. Next we find a 3/4" ID can or tube to fit around the
wire, but it's really thin thus cut
thru easily. Given this we add something to gap between the rope encasing
ferrule and the screw down clamp in adding
thickness and resistance to this twisting clamping pressure.
Given these details, why does
wire in plugs once they failed, often seem like the person that tightened the
plug did not ensure the
terminal was tight? In addition to the skin
effect of
current flow, remember expansion and contraction also. Might be someone was using a cordless drill or cordless screw
driver to tighten the screw terminals without verifying tension by
hand. Such tools reduces torque on the screw with each use due to less
voltage given off by the battery no matter the clutch setting - always verify the tension by
hand. Many times a clutch set cordless tool will click off but the
terminal will still be loose. Beyond this and important no matter if by
hand or by tool is another key factor - expansion and contraction. This especially the case both when over clamped and when used without ferrules. The
conductor in explained above will get hot by way of resistance. Hot metals expand. While they expand they tend to re-settle the stacking on individual conductors in pushing them out of the way. Once those conductors expanded that were pushed out of the way of other conductors that expanded more, when cool, they tend to make for a loose connection. Re-use this connection and it’s now high resistance no matter the installation torque. This especially the case when you put bare wires into a
terminal without the benefit of a
ferrule to keep the wires together. Some of them conductors will be cut, some clamped so they are solid with other conductors, some short of this
ferrule band will just be frayed and loose conductors.
While you do tend to want a tension device applied to
wire to be sufficiently tight not to come loose, you don’t want to over tighten them or be under tight given your theory of what’s tight is different than the standard. This is also why specific torque tensions is specified on most
plug instruction sheets. Something like 20 PSI for a 60 amp
stage pin plug as opposed to 120 PSF for a CamLoc
terminal. Given most of don’t have torque screw drivers or wrenches to be used, we and the industry in general relies upon the 1/4 turn past finger tight method in general. Given this
base of finger tight is something you have to verify against a known source - someone that by way of their own training has also been verified to have the right tension. Short of this it is torque wrenches in verifying your tension or feel for what’s what PSI in tension.
Given all of this, the
plug in question had a factory installed
crimp pin instead of a screw
terminal. More specifically, the company that manufactured the plugs onto the cable for me were using a four pin indent tool onto a
plug using a smaller sized pin cavity specifically designed for the size of a 12ga
wire to fit into it. This four pin indent tool costing big bucks, not only accurately crimps the
terminal with the accuracy you might expect of a expensive tool, but also in
crimping the
wire by way of all four sides to it tends to
crimp down onto the
wire very benevolent to it’s skin
effect. Unless the dial for
wire size on the
crimp tool was set for the wrong
gauge of
wire - up or down from 12
AWG, there is little to no chance the specific
plug in question had other than the proper and low resistance
crimp applied to the
wire attached to it. We can thus assume in seeing a crimped
terminal done by a pro company that it is the proper pressure on the
wire on this
plug and that it was done properly until proven otherwise.
Such
crimp terminals on the
stage pin plug is an alternative to the set screw and
ferrule method more normal to similar plugs given you need specialized gear to
crimp such things.
Hope this info gives out more info on the question and gives out more hints about the options for what went wrong, much less in general how such electricity flows down a
wire. Such areas that get hot are hot indeed either by arching or just resistance in general. This heat is dissipated outward from the source of the heat. As a overt hint, this might be a key factor in
tracking down the source for the heat, or as soundman says, “I would chop off the broken end and bad
wire and just make a new one as long as the
wire is up to standard.” Perhaps you might have found a key test as to one of the causes of the failure in better stating an observation as to what went wrong. Now it’s a question of if you note what you than would be studying and crossing out what things could not be the cause of the problem. Thus my also note of being on the cusp of the problem or rational for it's cause.