Some good responses to this thread, but I thought that in the sense of “Teach a man to fish” it might be useful to explain how to answer these kinds of questions when you don’t have access to Control Booth.
First some very basic ( simplified) electrical knowledge. When you have a light
bulb, you are passing electrons through a
wire into the
fixture. The force behind those electrons we
call Voltage. The number of electrons we
call Amperage. How bright the lamp is based on the Wattage of the lamp. All of these factors are interrelated by a formula ( W = V*A) IE The wattage of a device is the
Voltage times the Amperage. This is sometimes called the “West VirginiA” formula.
Now for must applications, what you have to worry about is getting too many amps in your wires or devices. If you put too many amps through a
wire, it will melt and cause a fire. In the old days the circuits in your
house had a
fuse. The
power to your wall
outlet went through the
fuse and if there were too many amps in the
circuit, the
fuse would melt before the
wire did. Today we have
circuit breakers that trip the
circuit ( IE interrupt the flow of electrons) when too many amps are flowing through it.
So let’s go through an exercise of “Can I fit 5 500
watt par cans on a
shoebox dimmer ).
The first thing to do is figure out the amperage of each
fixture you plan to use. We figure out the amperage by our formula ( W=V*A). Assuming 120 volts that would be “ 500 = 120 * A “ This gives a value for ‘A’ of 4.2 amps. ( Note – If you don’t have enough math to figure this out, please stop reading and do not try to figure this out yourself.)
If you are using a
shoebox dimmer with four dimmers, one of the dimmers will have two fixtures plugged into it. That
dimmer would have a total of 8.4 amps ( or 1000 watts) of load. Look at the spec for the
dimmer and see what is the capacity of each
dimmer . This may be expressed in amps, or in watts. If the value of each
dimmer is 1000 watts, ( 9 amps) you can
plug two fixtures into a
dimmer.
But we are not done yet. Let’s assume that you want to run all of your
par cans at full. This means that the
dimmer pack will be running 5*4.2 =21 amps / 5*500 = 2500 watts. If you look at spec for the
dimmer you are likely to see something like “ The maximum capacity of the
dimmer pack is 15 amps’ What is going on here is that the
power feeding the
dimmer typically uses an
Edison style
plug that is rated for 15 amps. If you put more amperage through it, it will ultimately melt. Sometimes you see one of these
shoebox dimmers with the ability to have two
feeder cables. So if you have one with two plugs on it ( each
plug feeding two dimmers) the
dimmer would work for your application. If not, you need at least two
dimmer packs. In either event you have two cables to
plug into the wall.
But wait, we are still not done yet. At this
point you need two sources of
power to drive your fixtures, in
shoebox dimmers this is typically a wall
socket. In most buildings, you will have a single 20 amp
circuit breaker controlling a number of wall outlets. If you have a standard duplex
receptacle, you can be pretty certain that there is a single 20 amp
breaker providing
power to both of the receptacles. So if you
plug both feeders from the dimmers into the same
receptacle, and run your fixtures up, you will be pulling 21 amps over a 20 amp
circuit breaker, and it will trip leaving you in the dark. You need to find two circuits that are controlled by different
circuit breakers and use them to
power your
dimmer packs. ( and that do not have major loads on them as well). If you have access to the
circuit breaker box, you can usually tell what receptacles are on what
circuit breaker by the labels in the panel. If you don’t have access to the
breaker box, it is probably a bad idea to try to do this since if you overload the
breaker, you will not be able to reset it.