Just clarifying:
1. There are no code violations in running open
DMX cable, correct?
2. Our S4's are 750w (at least they read 750 on the
barrel. I've never worked with 575w's but I always presumed that the 750 indicated 750w)
3. Where would one obtain
circuit breaker modules for the Sensor? Would our supplier have them?
Though
AHJ (see glossary) will take precedence,
DMX can probably be run open because it's low
voltage. However, there are sometimes specific ways you have to run the cabling. If you look above the
plenum ceilings in places, in many cases you'd find
ethernet and all sorts of low
voltage data/control cables that would just be sitting above the ceiling. However, firefighters started noticed when they would enter these buildings that as soon as the ceiling burnt up, the cables would
drop and become an obstacle to them. As such, now in many places it's required that these low
voltage cables not in conduits be secured in some manner, be it in a
basket or harness of some form. This may or many not be applicable to you, but understand that just because it doesn't have to be in a
conduit, doesn't then mean you can run it however you'd like. Also, you will not be able to run it in existing
line voltage conduits; if put in a
conduit it would need to be run in an individual
conduit containing only low
voltage wiring.
Any
Source Four rated for 750w, may also use 575w and 375w lamps. Also, they can use 77v 550w lamps with
dimmer doubling. The only difference is in the lamp, not the
fixture. If you want your fixtures to be less bright, or you can't afford to use as much
power, then you would lamp down to lower wattages. Also, 575w lamps burn through deep, saturated gels far slower than 750w lamps, and they do not burn gobos as quickly as well. Likewise, if all of your Source Fours are using 575w lamps and you some of them to be brighter, you would put a 750w lamp in. Most modern Source Fours are rated to 750w, but
PAR MCM's (metal cold mirrors) and
Source Four Juniors are only rated to 575w, and some older
Source Four products may contain lamp bases that are only rated to 575w, as that is how they were originally designed. The upgrade for those fixtures is simply a new lamp assembly.
Obtaining parts or products for your Sensor racks shouldn't be too difficult. Your dealers can probably hook you up.
ETC is a well-known manufacturer, and though dealers may not keep extra modules sitting on a shelf on site, many will have easy access to them that you could order the parts you need through them. However, I do not understand what you mean by "
circuit breaker" modules.
ETC makes many different products for their
dimmer racks that use
circuit breakers. If you're referring to a Constant-Circuit module (ex. CC20 = constant-on
circuit @ 20amps), then that is a module that will simply always remain active at
line voltage.
Another reason to consider
dimmer doubling though is if the fixtures on your
catwalk typically remain there. I know a couple theatres that have their entire catwalks on
dimmer doublers because they never have to worry about mixing their 77v and 120v lamps and fixtures up as the fixtures on their
catwalk almost always remain there.
Dimmer doubling is actually a very simple and relatively inexpensive option if the fixtures on your
catwalk are often static and wouldn't move to 120v positions regularly. As such though, I wouldn't recommend only a partial-upgrade. If you are going to
purchase dimmer doublers, get them for each and every
circuit on your
catwalk. If you have a mix of 120v and 77v fixtures up there, then there will be mistakes made in using the appropriate lamps at their respective voltages.