It is in a humid environment and at one
point there was leaking in that room. They put in a seperate AC
unit to maintain it at 65 constantly to eliminate that issue, but I know a lot of damage was done.
I cleaned the terminals and lightly polished the copper with some high grit sandpaper. They are making good contact with the
PCB. No change in behavior.
I hate to say it, but cleaning contacts with sand paper is a very bad idea. Things may look shiny, but I've seen many shiny and bright connections that were electrically lousy. If that was only done to high
voltage, copper to copper connections, then it probably did no harm. For cleaning big, copper connections I like to use Scotch-Brite 7447 or 8447 pads, then liberally flush with a cheap, low residue, aerosol contact cleaner. If sandpaper was used on low
voltage, low surface area connections, then I would be very concerned about embedded residues and scratches.
I don't know anything about the internal
layout of Sensor racks, but I have run into problems with electro-mechanical connection problems so many times in my career. Given the environmental issues the rack has been exposed to (high humidity, heat, salt air, pollution) I would bet that's the root cause here. Those conditions are ripe for oxidation, which is often invisible on tin and gold plated connectors. (This is an area where most tech support folks, that don't have much field experience, have no idea what happens to electronics out in the real world.)
Every low
voltage, electro-mechanical connection in the
system is suspect at this
point. Every card
edge connector, every ribbon cable, every socketed IC, every
pcb board to chassis, and chassis to chassis screw that might be relied upon for grounding.
The best way I know to clean connections is to flush with Caig
DeoxIT D5. If any low
voltage connections that got the sandpaper treatment, they should be scrubbed with a clean, cotton cloth or
cue tips wetted with D5.
The D5 will go all over, and leave a residue, which does not hurt anything, so don't be afraid to be messy with it. The main thing is to flush contaminants away.
After the D5 drys for a few minutes coat with
DeoxIT G5, which is a protectant.
Residues will eventually dissipate.
I cannot over emphasize the good results I have had from the Caig products. They work when others fail and are essentials in my electronic tool box.