So we're seeing an intermittent input error from port A on our Sensor. This rack has had some issues that we've mostly resolved over the past few months. Initially we had a CEM with a bad zero cross detector on phase A. After sending it back and forth a few times we were not able to fix it (though ETC bench tested it and said it worked fine with them- which I do believe). For some reason it wouldn't work right in our rack, but would elsewhere. The real kicker is that the borrowed CEM worked fine. Fast forward to a lightning strike which trashed our arch controller. Troubleshooted that problem down to the transceiver IC's on the stations and on the DAS controller. Replaced and got it running again.
Now we are getting this intermittent error, only on Rack 1 (the troublesome one). I swapped CEM's and it initially didn't follow, leading me to reason that it might be a problem with the terminal contacts on the CEM or the backplane. Since we experienced trouble with a particular known-good CEM, but no trouble with a separate good CEM, perhaps the problem might be in the connections. Perhaps corrosion or debris on the terminals. Cleaned the CEM terminals with isopropyl alcohol and blew out the connector on the back plane per ETC tech support and the problem seemed to leave us. Until today.
Now the same CEM (still moved into rack 2) is exhibiting DMX port A input errors. With these errors comes a flickering to full of random dimmers, not favoring a particular phase that I can see. It also seems prevalent when a lot of dimmers are at mid-levels, but it might just be that it's more noticeable under those circumstances.
It comes and goes intermittently. As I am typing this I'm getting a "System OK" display.
Other troubleshooting included changing our controller. Changing the cable going from the controller to the wall. There are three input ports in the building, I haven't attempted using anything but the furthest at this point. That will be my next troubleshooting.
I also noticed that the same transceiver chips are on the CEM (SN7517) that are also on the interface PCB's with the arch controllers. I had a couple of spare new ones that I tried swapping into the CEM. Though I'm not sure that they are used in the DMX side of the interface, I figured it wouldn't make anything worse at this point. It still had errors when I powered back on, but they have since stopped. Not sure if that made a difference or not.
I do plan on calling tech support, but I figured I'd poll the booth for any help here as well. Frustration abounds.
Now we are getting this intermittent error, only on Rack 1 (the troublesome one). I swapped CEM's and it initially didn't follow, leading me to reason that it might be a problem with the terminal contacts on the CEM or the backplane. Since we experienced trouble with a particular known-good CEM, but no trouble with a separate good CEM, perhaps the problem might be in the connections. Perhaps corrosion or debris on the terminals. Cleaned the CEM terminals with isopropyl alcohol and blew out the connector on the back plane per ETC tech support and the problem seemed to leave us. Until today.
Now the same CEM (still moved into rack 2) is exhibiting DMX port A input errors. With these errors comes a flickering to full of random dimmers, not favoring a particular phase that I can see. It also seems prevalent when a lot of dimmers are at mid-levels, but it might just be that it's more noticeable under those circumstances.
It comes and goes intermittently. As I am typing this I'm getting a "System OK" display.
Other troubleshooting included changing our controller. Changing the cable going from the controller to the wall. There are three input ports in the building, I haven't attempted using anything but the furthest at this point. That will be my next troubleshooting.
I also noticed that the same transceiver chips are on the CEM (SN7517) that are also on the interface PCB's with the arch controllers. I had a couple of spare new ones that I tried swapping into the CEM. Though I'm not sure that they are used in the DMX side of the interface, I figured it wouldn't make anything worse at this point. It still had errors when I powered back on, but they have since stopped. Not sure if that made a difference or not.
I do plan on calling tech support, but I figured I'd poll the booth for any help here as well. Frustration abounds.