Seven.
I used the same method but round up so 10
Yes 32 amp 3 pin with 3 phase.
In the absence of useful details about 3 phase or otherwise, the best answer we can give is this:
On each phase, you can run 7 1000w lamps if you are not running them continuously for more than 3 hours.
If you are running them conitnuously, or are using 120v PAR64 lamps in series, then you can connect 6 per phase.
If you truly have a 3 phase connection with neutral, this means you can run 18 or 21 lamps maximum from the outlet.
You should be aware of what the size of the incoming supply to DB box you mentioned is, if you are planning to load more than one socket, but the whole box only has say a 50A supply, then the main breaker will trip long before you reach the maximum loading on 2 outlets...
Now that ive explained in detail to the best i could, how many 1000w pars can i put on each 32a socket ?