Is it possible (or acceptable) to use 2P&G (stage pin) to carry 208 volt three-phase?
These 100 Amp Stage Pin Plugs made exclusively for 250V circuits differ from the 125V plugs by color and pin configuration.
1. The ANSI E1.24 standard for stage pin connectors requires that the connections to the connector are
--Ungrounded conductor (hot)
--Grounded conductor (neutral)
--Grounding conductor (equipment ground)
2. The 20 amp pin connector is dual rated 125/250V. However, (1) above applies to all voltages. So the only place that the connector could be used at voltages higher than 125V is in 230/240 markets where the neutral is still connected to one of the pins.
3. The UL489 connector standard now references E1.24 for stage pin connectors.
4. A stage pin connector is not rated to carry three-phase power under any circumstances.
ST
Because no one has yet asked: what are you trying yo do, OP?
Does E1.24 not consider the 2P&G-60A/240V and 2P&G-100A/240V variants, as manufactured by Union Connector, Group 5, and (possibly) others?
Nothing specific, I was just wondering. And I'm wondering because I actually SAW a NEMA 6-15 receptacle labeled "208 VOLTS", so I didn't know if 208 Volt 3ph. could be carried on 3 conductors. I didn't think so, but then again, I don't know everything about 3 phase power, so there you go.
Does E1.24 not consider the 2P&G-60A/240V and 2P&G-100A/240V variants, as manufactured by Union Connector, Group 5, and (possibly) others?
This one sports an ETL listing:
Group5 100 Amp/220 Volt Female Inline DSS (yellow) | Marinco
-----
There's a regional lighting company from Florida I believe that uses the 2P&G-20 to carry bi-phase power for its moving lights. Seems like bad practice to me.
See also the thread http://www.controlbooth.com/forums/lighting-electrics/27205-using-208v-nema-5-15-a.html .
Seeing a NEMA 5-15 receptacle labeled 208 volts would be a serious code violation, and extremely dangerous, as the 5-series of devices is 120 volts only - one hot, one neutral.
It's not particularly funny, nor trivial. The danger doesn't come in the form of a piece of copper turned sideways, but the violation of the keying system that prevents devices from being plugged into the wrong voltage and/or current service. This is a significant fire/life safety issue - putting 208 volts into your space heater, hair drier, light fixture, motor, etc. can not only cause equipment damage, but kill you and/or burn your building down....Which is funny, since the only real difference is the blade orientation. 6-15 has collinear blades, a 5-15 has parallel blades. I think a 5-15 would handle 208V just fine, but the code compliance makes sense: The blade orientation keeps someone from plugging a 120V device into a 208V (or 240V, for that matter) circuit. Thus, I don't think it would be "extremely dangerous". ( Illegal, yes.)
...Which is funny, since the only real difference is the blade orientation. 6-15 has collinear blades, a 5-15 has parallel blades. I think a 5-15 would handle 208V just fine, but the code compliance makes sense: The blade orientation keeps someone from plugging a 120V device into a 208V (or 240V, for that matter) circuit. Thus, I don't think it would be "extremely dangerous". ( Illegal, yes.)
ive done it before without issue, i had a distro box with stagepin outlets and needed to power up a water heater that needed 208v all we did was switch the banded feeder around and put a hot where the neutral should have been on the distro then changed the connector on the female end of the 20 amp cable so the water heater could plug in. it worked fine without an issue and ran for over a month.
copper is copper.
ive done it before without issue, i had a distro box with stagepin outlets and needed to power up a water heater that needed 208v all we did was switch the banded feeder around and put a hot where the neutral should have been on the distro then changed the connector on the female end of the 20 amp cable so the water heater could plug in. it worked fine without an issue and ran for over a month.
copper is copper.