Thank you! haha now just a couple more questions
1,whats the difference between Three
Phase and Single
Phase?
2,I see that it has direct
ethernet input. So does that mean if I have a newer board that has
ethernet output I can run it straight to the rack? And if so can I run in with
Ethernet and out with
DMX into another
fixture or rack? Or can I run in with
Ethernet and out with
Ethernet?
3, What cable runs out of the rack to the lights? Is it
Socapex? Or another kind? If there is another kind.
4, Is a
Dimmer Doubler just makes it have two outputs instead of having to
twofer?
5, What are these options:
Amp-Trap®
fuse
Bussing kit for 2 - 12-module racks
19" Auxiliary Rack(s) for 12-module rack
Sorry for so many questions:
neutral:
[6]What happens if you do overload the circut?
[7] And the
AFM module, is that just like an extra fan to keep it cool???
Question 1: I would encourage you to search this forum as there have been several threads on it. Search results for
Three phase vs. Single Phase
Question 2: This will depend on which control module you are talking about. If it is the
CEM classic, the port on the front is an RJ45
connector, but is not actually using
ethernet nor networking
protocol. If it is a
CEM+, the
CEM+ will listen to EDMX (ETCNet2) or
sACN (streaming
ACN) for its control signal. If you have a
console that outputs either of those two protocols onto your lighting
network, then you can connect straight to the rack through a
switch and control your lighting rack. As for coming in with
ethernet and out with
DMX, this is a complicated yes. That feature is something that a service technician should setup for you.
Question 3: Usually in install racks, it is simply building
wire gauged to the appropriate size for the
circuit. It is not usually multi-conductor cable as that is both expensive and usually hard to pull through
conduit.
Question 4: Sort-of. It takes the sinewave of the
power coming on the
circuit and splits it so that the top half of the sinewave becomes A and the bottom half becomes B. This means that roughly half of the
voltage is used by one side and the other side uses the other half. To use this feature, you will need the special
Dimmer Doubler
two-fer as well as 77V lamps in your Source 4 Fixtures that are connected to these circuits.
Question 5: Amp-Traps are used when the rack is being
fed more
power than it is rated for (usually in situations where multiple racks are being
fed off the same incoming source). We do not recommend this, but there are situations in places where it is necessary.
A bussing kit is used when you have two (or more) racks powered from the same feed. It passes the
power from the buss bar in rack 1 to the buss bar in rack 2, 3,
etc...
An Aux Rack is used to give more space for the electrician to land the incoming feed
wire. It can also
house a main
circuit breaker so that the rack's
disconnect is right next to it saving time in trying to figure out where the d**n
breaker is located.
Question [6]: Ideally, the
breaker will trip stopping the potential for fire and other bad things from happening. Because each
breaker has a little
bit of wiggle room in the amount of overcurrent it takes to trip, you can also potentially damage the
power cube in the
dimmer module if you stay in that state for a long enough period of time. (A
power cube is the
SCR/
SSR/
Triac/
etc... that controls how the module dims)
Question [7]: The
AFM is a blank put in place to maintain the proper airflow of the rack. The fan at the top draws air through the door and filter, (which should always be kept closed when not accessing the modules or control module,) up through the rest of the modules, and out the top. This is necessary to keep the dimmers from overheating.