Running Cat5 directly into Ion

Discussion in 'Lighting and Electrics' started by StephIsabel, Nov 9, 2015.

  1. StephIsabel

    StephIsabel Member

    Messages:
    10
    Likes Received:
    3
    Occupation:
    ATD/Production Coordinator/LD/Educator
    Location:
    Easton, Pennsylvania, USA
    Hi all,

    I have a very low-end LED controller with Cat5 ports that I am trying to run directly into an ETC Ion. I can't seem to make the light board see the controller, although the controller claims it can go directly into any DMX control system. I have tried all of the deep settings in the shell of the Ion to no avail. Anybody run into this problem?
     
  2. SteveB

    SteveB Well-Known Member

    Messages:
    4,395
    Likes Received:
    1,358
    Location:
    Brooklyn, NY
    Nothing is broken.

    The Ion console does not accept DMX input from another console. I assume you might be trying to read DMX or other channel values from the other console ?, to use somehow in the Ion ?.

    The LED controller information about DMX means it can talk to dimmers and other devices that use DMX as the method to receive console data.

    Ion, being another controller, has no method to interface with a console via another consoles DMX output. Ion can interface on an ETC Net 2 or sACN network with assorted other devices via the Cat5 port. In that setup it can work with ETC remote focus units, a WiFi router and other devices running compatible software (iOS remote console software, same in Android, or OSC controls), as well as dimmers, other ETC consoles (as backup as example), as well as gateways and nodes outputting DMX to dimmers and devices.
     
    Last edited: Nov 9, 2015
  3. derekleffew

    derekleffew Resident Curmudgeon Senior Team Premium Member

    Messages:
    4,845
    Likes Received:
    3,455
    Location:
    Las Vegas, NV, USA
    I'm guessing that, rather than "controller," you mean an LED power supply, or "brain" that uses RJ-45 connectors instead of 5pin XLR for its DMX. (See DMX-over-CAT5.) You need to buy or build the proper adapter. Note there are various "standard" pin-out s.
     
  4. BillConnerFASTC

    BillConnerFASTC Well-Known Member

    Messages:
    5,696
    Likes Received:
    2,839
    Occupation:
    Theatre Consultant
    Location:
    Clayton NY 13624
  5. lwinters630

    lwinters630 Well-Known Member

    Messages:
    724
    Likes Received:
    237
    Location:
    west of Chicago
    I believe this means out of the controller and into a dimming rack or other DMX INPUTS. The Ion is an output.
     
  6. DuckJordan

    DuckJordan Well-Known Member

    Messages:
    2,734
    Likes Received:
    282
    Location:
    Doesnt matter
    Color of jacket on cat5 is not standard. The special connectors have been called cross over cable but I don't believe every device can handle direct connections.

    However what is likely happening here is he has an LED driver for an LED strip that uses cat5 as the input for dmx. I've seen a couple of these pop up once in a while so all that's needed is to find the pinout of the device and make a dmx adapter to change from 5 pin or 3 pin whichever you are using to Ethernet.

    Sent from my XT1060 using Tapatalk
     
  7. WVTheatre

    WVTheatre Member

    Messages:
    71
    Likes Received:
    1
    Location:
    Chicagoland Area
    Bill has the answer. You need to connect both devices to a network switch (not on the internet please!) for this to work. Otherwise the typical colour for a "crossover" cable is a yellow jacket (though standard patch cables do come in the yellow variety, they simply will not work!). Hope this helps.
     
  8. BillConnerFASTC

    BillConnerFASTC Well-Known Member

    Messages:
    5,696
    Likes Received:
    2,839
    Occupation:
    Theatre Consultant
    Location:
    Clayton NY 13624
  9. AlexDonkle

    AlexDonkle Active Member

    Messages:
    283
    Likes Received:
    45
    Occupation:
    Consultant
    Location:
    New York, NY
    Just to add, crossover cables are no longer needed for most modern equipment. Auto MDI-X is now built into most equipment to automatically detect the cable type used and compensate for it.
     
  10. WVTheatre

    WVTheatre Member

    Messages:
    71
    Likes Received:
    1
    Location:
    Chicagoland Area
    True. Though crossovers are always my first thought (thanks to the guys @cisco for beating it into my head), especially when dealing with older devices.
     
  11. SteveB

    SteveB Well-Known Member

    Messages:
    4,395
    Likes Received:
    1,358
    Location:
    Brooklyn, NY
    This is what I call a "ghost post'.

    A week and a half of answers and no further comments or questions from the OP.
     